ac doesn't come on, and internal house blower motor does not turn on, in the on position, turn it back to auto.

replaced capacitor with another one (not the same, but all I could find, with 45/5 for dual use)

Turn all breakers back on (none had been tripped) and nothing.

Replaced battery in thermostat, ended up junking the thermostat and buying a new one.. put that in, with new batteries, and nothing. Thermostat calling for cool.

Order a new blower motor assembly.. while waiting for it to arrive, it's been 4 + days, I am running a portable AC unit in the interim, when all of a sudden, the ac, which has been in the on position and calling for cool for 4 days, all of a sudden starts working.

Thoughts?
 

4.6.3

All-Conference
Jun 4, 2022
1,040
1,092
113
ac doesn't come on, and internal house blower motor does not turn on, in the on position, turn it back to auto.

replaced capacitor with another one (not the same, but all I could find, with 45/5 for dual use)

Turn all breakers back on (none had been tripped) and nothing.

Replaced battery in thermostat, ended up junking the thermostat and buying a new one.. put that in, with new batteries, and nothing. Thermostat calling for cool.

Order a new blower motor assembly.. while waiting for it to arrive, it's been 4 + days, I am running a portable AC unit in the interim, when all of a sudden, the ac, which has been in the on position and calling for cool for 4 days, all of a sudden starts working.

Thoughts?
Was it running continuously for a while before it quit? Did you notice if any of the condensate lines were iced up?
 
  • Like
Reactions: SuperBigFan69

4.6.3

All-Conference
Jun 4, 2022
1,040
1,092
113
as it sat for 4 days? I don't think so.. yes, I'm grateful it started working, but now I don't trust it, why did it fail and sit there for 4 days laughing at me.
It could be SO many different stupid little things. Do you own a multimeter? Not a Menards meter.. I’m talking a legit meter.
 

WTFMatt

Senior
Feb 14, 2010
991
837
93
Keep an eye on it. If it stops working again, you may very well have a refrigerant leak in the evaporator coil. It could have frozen the coil and just took awhile to dethaw.
 
Last edited:
  • Like
Reactions: NikkiSixx

NikkiSixx

Senior
May 31, 2022
842
859
93
Was it running continuously for a while before it quit? Did you notice if any of the condensate lines were iced up?
I didn't notice anything like that. It quit early in the morning, around 7:30 am.

The first thing I did was take a shop vac to the drain line, using my hand to make a seal, to suck out anything that might be clogged.

That didn't seem to help, although I did get about a gallon of slime water out of the line.
 

NikkiSixx

Senior
May 31, 2022
842
859
93
It could be SO many different stupid little things. Do you own a multimeter? Not a Menards meter.. I’m talking a legit meter.
I just purchased a new multimeter, strictly to get the capacitance feature, as my cheap one doesn't have it.

Old Capacitor measures 5.12 on fan side, herm side 43.40

I think it's okay, although it is out of the unit at the moment. mfg stamped with 0422, so I assume it was made in april of 2022 and replaced sometime in late 2022+
 
Last edited:

NikkiSixx

Senior
May 31, 2022
842
859
93
Keep an eye on it. If it stops working again, you may very well have a refrigerant leak in the evaporator coil. It could have frozen the coil and just took awhile to dethaw.
is there anything I can do to get ahead of this or to be more proactive?

I assume if I call a guy to come out to test for leaks, he's going to tell me to replace the unit (mfg in 2016) so it's approx 9 years in service in florida, but I really don't have an extra 8k sitting around to drop on a new system.

It's a goodman system, doesn't appear to be any circuit boards.. there is a transformer i could replace, and the contactor (not sure what it's called) but outside next to the capacitor, is the switch to start the outside compressor.. i could probably replace that part as well, but it seems to function ok from a physical stand point. I can press the contact and it starts the motor, but it's an electrical switching to physical switch I think.